We are having continuous problem with our dechlorination analyzer. I've heard alot of good things about the ATI reidual sulfite analyzer. Does anyone have experience with this unit?
Post #8518
Posted 2/28/2008 3:15:28 PM


Supreme Being

Supreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme Being

Group: Forum Members
Last Login: Today @ 6:54:35 PM
Posts: 235, Visits: 617
We have 2 units for SO2.  Way less headaches that brand X&X.  We had to change our permit so a bisulfite residual = zero chlorine and a zero bisulfite = our pre-dechlor Cl2 residual with no credit for partial de-chlor.  It uses cheap sulfuric acid as its only reagent.  You MUST install a line bleaching system.  We have an automated 3 way valve that back flushes the sample line at 20 mg/l Cl2 and a pretty good velocity.  Otherwise slime builds up rapidly that lives off the SO2, reducing the value the instrument reads causing you to overdose.  Cl2 also reacts to the slime and it sloughs off resulting in high TSS values if you don't chlorinate your lab sampler line.  We have gone to ATI for Cl2 also.
Post #8527
« Prev Topic | Next Topic »


Reading This TopicExpand / Collapse
Active Users: 1 (1 guest, 0 members, 0 anonymous members)
No members currently viewing this topic.

PermissionsExpand / Collapse

All times are GMT -5:00, Time now is 10:53pm

Powered By InstantForum.NET v4.0.0 © 2008
Execution: 0.094. 10 queries. Compression Enabled.