Has anyone used a chlorine electrode to control their chlorinator. If you have what brand and how well did it work.

JJ

Post #5134
Posted 5/15/2007 2:45:07 PM


Supreme Being

Supreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme Being

Group: Forum Members
Last Login: 8/19/2008 3:11:27 PM
Posts: 75, Visits: 529
We had Wallace and Tiernan chlorine analyzers. They never worked well - our chlorine residual was never consistant. Calibration was difficult, the analyzers were not user friendly. Maintainance on the probes was a nightmare. We have since taken the analyzers out of service, switched from gas to sodium hypo, and manually make our adjustments. Much easier!
Post #5139
Posted 5/15/2007 6:50:00 PM


Supreme Being

Supreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme Being

Group: Forum Members
Last Login: Today @ 12:09:39 PM
Posts: 248, Visits: 660
By definition total chlorine is the measure of what oxidized KI to I2 at pH 4.  Steer clear of any chemical free electrode, it may be able to measure free chlorine, but you need KI and pH4 to measure total chlorine.
Post #5145
Posted 6/25/2007 12:03:30 PM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: 7/21/2008 11:29:39 AM
Posts: 3, Visits: 3
We chlorinate with sodium hypochlorite and dechlorinate with sodium bisulfite. We monitor both location with in-situ ProMinent Dulcometer chlorine residual probes. Readings are fed backe to a PLC as part of a compound control loop to regulate chemical feed. Have been using them since 2003 and have worked fairly well. We didn't want analyzers with chemical reagents to minimize maintenance. We check calibration weekly which is a fairly simple procedure. Change membranes and electrolyte in probes every 6 months or so. Residual readings vary slightly when compared to wet analysis but we have found that the accuracy is satisfactory for our process control needs.
Post #5639
Posted 7/2/2007 1:11:59 PM


Supreme Being

Supreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme Being

Group: Forum Members
Last Login: Today @ 12:09:39 PM
Posts: 248, Visits: 660
Do you have ammonia in the sample?
Post #5722
« Prev Topic | Next Topic »

Reading This TopicExpand / Collapse
Active Users: 1 (1 guest, 0 members, 0 anonymous members)
No members currently viewing this topic.

PermissionsExpand / Collapse

All times are GMT -5:00, Time now is 9:56pm

Powered By InstantForum.NET v4.0.0 © 2008
Execution: 0.141. 10 queries. Compression Enabled.