Anybody have any feedback on experiences with TROJAN UV? Likes / Dislikes! Any plants in KS, MO have TROJAN UV system in place?
|
|
|
|
yes we have the second biggest one it is a 300 plus and it sucks and not joking very expensive to run and not real good at dealing with and extra soilds loading if you have any operatioal problems or even winter. op's it would work great with filters a head but if not the best look to europe they are taking it out>>> and going with ozone.
|
|
|
|
Transmittance testing is very Important when making the leap to U.V. sterilization. Effluent transmittance #s should be no less than 60 when doing the testing. The lower the #s the more Hydro and more expensive the unit is going to be and more Maintenance cleaning the bulbs and fouling of the bulbs requiring changing more often, otherwise there should not be any problem. The only thing I don't like is the fact that you cannot do a residual like Chlorine, you are at the mercy of waiting for the test results from the Lab which takes a few days. Takes a little getting used to but seems to be relatively trouble free. Trojan is the only unit I'm familiar with.
|
|
Joined: 9/21/2009 Posts: 98
|
The thing about UV is that to maintain the proper dosage you must maintain a constant amount of TSS as they block the energy penitration. If you have a backup chlorine system you could feed a small amount of chlorine during the higher TSS episodes. There is a good synergy effect.
Chlorine residual may give you a false sense of security as different forms of combined chlorine have varied disinfecction properties. I just operate the plant maintain a constant chlorine dosage that I know will give me good results at the current contact time. As flow increases you adjust the chlorine dosage higher as the contact time is reduced.
Monitoring the UV transmittance is important, as lower transmittance effectively reduces the energy dosage, and adjustments must be made. Normal variation in %T should be known prior to committing to UV disinfection.
|
|
Joined: 10/25/2011 Posts: 1
|
We are starting up a new UV system and are having difficulty with consistent UVT readings. The results are stable for several hours then rapidly - over a few minutes swing from 70 to 50 or lower several times for a few hours - then stable again. Water quality does not appear to change. The rapid swings results in all the banks turning on at 100% since it is below the validation range of 55, or dosage higher than what would be expected. We do not yet have a portable UVT to confirm the values. What has been your experience with consistency of UVT results and do you have a favorite UVT meter manufacturer?
Thank you for your help.
|
|
Joined: 12/15/2009 Posts: 5
|
complicated and costly. If you have a good I.T. guy to keep all the bell and whistles going it has the potential of working well.
|
|
|
|